In Chapter 9 at Table 1 in the "over 2 conductors" column, I'm using 40% conduit fill.
Over 40% for a 3" schedule 80 pvc is 2.577 square inches.
4/0 RHW-2 = 0.4754 each times 4 = 1.9016
2/0 RHW-2 = 0.3505 each times 2 = 0.701
These two figures total 2.6026 which is 0.049 over.
So 2 sets of paralleled conductors (200 amp urd) in 3" is over.
The conduit length from the padmount to the service pedestal is 20 feet. Does derating apply? If so, where is this in the code?