2 sources of Power in same conduit ?

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Can 277V circuits and 120V circuits from two different sources (and serving two different loads) be ran in the same conduit?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Dave done all of the time. There was a time several code cycles ago a requirement for the neutral of one of the systems to have a stripe. Simple white and gray colored neutral conductors weren't enough.
 

tank728

Senior Member
Location
New Jersey
Occupation
Electrician
I agree with Dave done all of the time. There was a time several code cycles ago a requirement for the neutral of one of the systems to have a stripe. Simple white and gray colored neutral conductors weren't enough.
Does your company do this often?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
They can, but there is a code section that requires you to label the j-boxes with each circuit number and source notifying anyone else that you have two different sources present. I can’t think of the code #.


Sent from my iPhone using Tapatalk
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
They can, but there is a code section that requires you to label the j-boxes with each circuit number and source notifying anyone else that you have two different sources present. I can’t think of the code #.


Sent from my iPhone using Tapatalk
I thought that label was only if there was a circuit ran through another panel. I'd like to know the code if that's a requirement for junction boxes though?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
They can, but there is a code section that requires you to label the j-boxes with each circuit number and source notifying anyone else that you have two different sources present. I can’t think of the code #.


Sent from my iPhone using Tapatalk
I'll believe it when you can tell us the section. Heard that enough times.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I'll believe it when you can tell us the section. Heard that enough times.

210.5(C)

I was incorrect stating you have to put the circuit # but you do have to identify the different voltages in some way, and either the box must be labeled or you have to post somewhere what your method is

Sent from my iPhone using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
210.5(C)

I was incorrect stating you have to put the circuit # but you do have to identify the different voltages in some way, and either the box must be labeled or you have to post somewhere what your method is

Sent from my iPhone using Tapatalk
Ok.
That applies to terminations, connections, and splice points. So conductors that pass through jboxes are exempt. Boxes don't need the method posted, only panelboards or 'similar distribution equipment'.
I thought that the circuit # thing was wrong.
Also this applies to branch circuits, 215.12(C) has the same language repeated for feeders. (Why isn't this just said once somewhere, like in 110?)

Of course it's good practice to use different color wires for different voltage systems, and saves time. I think most people do that for branch circuits at the least.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The only "no" I can think of is legally required standby circuits

Sent from my moto e (XT2052DL) using Tapatalk
That would apply to emergency circuits, but it does not apply to legally required standby circuits.
701.10 Wiring Legally Required Standby Systems.
The legally required standby system wiring shall be permitted to occupy the same raceways, cables, boxes, and cabinets with other general wiring.
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
Can 277V circuits and 120V circuits from two different sources (and serving two different loads) be ran in the same conduit?
I don't recall that ever being legal in california nor would I consider doing it myself , although as mentioned above many seem to accept the practice. Typically it use to be 1 single or three phase system single or multiple boat would be allowed within a conduit from the original source it was fed from, no combining various panels to one conduit. The exception was normal power and emergency power normally found with egress lighting systems.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Can 277V circuits and 120V circuits from two different sources (and serving two different loads) be ran in the same conduit?


Sent from my iPhone using Tapatalk
I don't recall that ever being legal in california nor would I consider doing it myself , although as mentioned above many seem to accept the practice.
300.3(C)(1)
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
I get the 600v insulation concept but I truly thought mix matching voltages from other sources was a no ..no.
I doubt I'd ever do it anyway unless I'm in a sort of bind, were it made most sense. I can see its benefit with a needed nearby pull box .

Maybe it was a usual spec on a school or hospital project years back ..
 