Emergency is Art 700, Legally Required is Art 701. “Life Safety” branch gets broken down in Art 517Life safety Art 700.
Emergency is Art 700, Legally Required is Art 701. “Life Safety” branch gets broken down in Art 517Life safety Art 700.
Article 517 falls under hospitals. There is life safety panels in establishments other than hospitals, in which, the code will fall under article 700. In Legally required, A701 and Optional, A702, u can have 2 sources of power, emergency or normal, in the same raceway but u r not allowed if its Life Safety.Emergency is Art 700, Legally Required is Art 701. “Life Safety” branch gets broken down in Art 517
My comment was you said Article 700 was Life Safety, It’s Emergency. Article 701 is Legally Required, not “Life Safety”, and that the Life Safety branch was part of the Essential Branches in Art 517, hospitals.Article 517 falls under hospitals. There is life safety panels in establishments other than hospitals, in which, the code will fall under article 700. In Legally required, A701 and Optional, A702, u can have 2 sources of power, emergency or normal, in the same raceway but u r not allowed if its Life Safety.
and after you connect them together they are effectively one and the same. Grounded neutrals however since they are current carrying are not one and the same. If "shared" it will work, but will carry two different currents at same time which depending on circumstances and (ignoring that code likely won't let you "share" the conductor one would possibly need to more carefully calculate the heating effects of the combined currents when selecting conductor size.Nope. They would be required to be connected together when complying with 250.148.