#2 URD Direct burial
Buck Parrish
NC & IN
I don't use URD very often . I am estimating a horse barn. The guy wants a 100 amp panel. He even went as far to upgrade his home service to 400 in preperation to go to 100 amps for the barn.
So this would be a feeder from his home panel. That dis - allows 310. 15b
I told him the ampacity of #2 has been reduced to 80 amps.
Am I right ?
Do you have to use the 60 degree column with direct cable. I know lots of states still allow it on a 90 due to the fact thier on the 05 code.
Which is right in NC under NEC 08? Is it 80, 90 or a 100 amps. Thanks in advance.
The problem is URD isn't in the NEC, so you need a recognized or dual-rated insulation type.
Buck- Hunt sells #2 aluminum direct burial that is dual rated and cost $1.18/ft. It has 3- #2 and a ground. It is rated 90amps at 75C. This is not se cable but USE cable so it doesn't fall under the 60C. The wire at Hunt is RHW & RHW-2.
The last one I did I thought they were going to make me add bonding grids to the existing barn. Read Art 547 before you bid it.:D
Make sure you and your inspector understand what's required for an equipotential bonding grid if there will be any concrete slabs where livestock stand.
We're in the process of wiring a large dairy barn. All slabs have mesh/rebar in them. We also have to hit any isolated metal fencing/metal troughs/gate posts, etc and bond them to the mesh.
The Burndy crimps we're using to tail #8 copper from the concrete mesh are $3 apiece. We've used about 400 so far....
And a ton of rebar clamps too....
If your barn is all dirt floors, you got it easy!
Read 547.10(A) carefully, just because there is a concrete floor does not automatically mean an equipotential grid is required.
Am I right ?
As for the size of conductor needed what is the load calculation? Same goes for whether upgrading the service to 400 amps is needed or not - just because you put a 100 amp panel in the barn does not mean you added 100 amps of load. If small barn with only a couple horses you may find that your load calculation is only 20 - 30 amps, or even less.