roger said:And I agree, if the intentent was for all receptacles in a bath room to be supplied by a 20 amp circuit, 210.11(C) should have included the word "all" (as 210.12(B) does) instead of the words "at least one".
Roger
I agree with Roger by the first statement of 210.11 (c) (3) " in addition to the number of branch circuits requried by other parts of this section". As long as you have met the 1 20amp. circ. rule I cannot see where it is prohibited to have a 15 amp. circ. It's no different than 210.11 (c) (2) for the laundry. As long as I have the 1 20amp circ. and I do not leave the laundry room with it, I can put as many 15 amp circ. in the laundry room as I want. Which takes us back to what Bob said about the 30 amp circ. for the dryer. And to throw gas on the fire 210.11 (c) (2) doesnt tell me where to put the 20amp circ. except in the laundry room. It makes no mention of plugging in the washing mach. Now would I be negligent in not installing the 20 amp. circ so the washer could be plugged in, yes. would it be a bad layout on my part, yes. Could I put a 15amp circ. for the washer and have the 20amp circ. on a opposite wall from the washer? I think so.