Just the dishwasher's going in for now,
Instead of a 15 amp circ. I brought over a 20 in case he wants to add a disposal in the future.
Does an installed receptacle on the "20 amp" breaker, chord connection to the DW protect the DW as required ???
Thank you
you're welcome. most DW are hardwired so you arent going to be able to connect it via a cord to a receptacle. We usually leave ~6' of #12 NM coiled up on the floor where the DW goes, that way there is enough slack to remove it w/o undoing the connection.
Considering the reason the DW GFCI requirement was put into the NEC I would use a GFCI.
Or maybe the gfci :- )
Single receptacle ?? If a single on the 20 amp circuit it would need to be a 20 amp single recpt then ?
you're welcome. most DW are hardwired so you arent going to be able to connect it via a cord to a receptacle. We usually leave ~6' of #12 NM coiled up on the floor where the DW goes, that way there is enough slack to remove it w/o undoing the connection.
Probably in the NJ Rehab Code if you're doing a remodel. I thought if it was new construction you still had to GFCI/AFCI protect it. The last time I hardwired a DW the EI told me I had to install a breaker lock for it. So, I've been cord and plug attaching DW's ever since as long as they're installed adjacent to the sink cabinet.Good point. I'm trying to find the NJ amendment that still allows for a single receptacle to be used in lieu of GFCI protection.
Probably in the NJ Rehab Code if you're doing a remodel. I thought if it was new construction you still had to GFCI/AFCI protect it. The last time I hardwired a DW the EI told me I had to install a breaker lock for it. So, I've been cord and plug attaching DW's ever since as long as they're installed adjacent to the sink cabinet.
As far as installing a switch for the disposal, if the HO buys a batch feed type unit, once you insert the drain cap and twist it the disposal comes on.. If you'd rather use a switch then using an GFCI/AFCI breaker will allow you to split wire a std. duplex receptacle. Too much work as far as I'm concerned.
There isn't one, 210.8(D) was adopted without modification so a GFCI protected circuit is required. Just be careful if the dishwasher recommends a dedicated circuit then there would be a problem with sharing it with a disposal.Good point. I'm trying to find the NJ amendment that still allows for a single receptacle to be used in lieu of GFCI protection.
There isn't one, 210.8(D) was adopted without modification so a GFCI protected circuit is required. Just be careful if the dishwasher recommends a dedicated circuit then there would be a problem with sharing it with a disposal.
Understandable they really mess with 210.8.After checking the NJ amendments again I agree with you that the GFCI protection is required. I will correct my earlier post.