It is true that Canada doesn't require 20 amps in a bathroom and that theoretically you can do an entire home with 15 amp circuits however it is seldom done that way. If you use 15 amps in a kitchen then you have to split wire the device and have 2- circuits to the receptacle.

A comment from a Canadian
We have no requirement for 20 amp in bathrooms. I think you do. 20A is common in kitchens but we have the option for 15A splits (3 wire with the bridge removed in the duplex receptacle). Splits aren’t very common because GFCI protection requires a breaker. Theoretically, we could wire a house with no 20A receptacles but it’s never done.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
It is true that Canada doesn't require 20 amps in a bathroom and that theoretically you can do an entire home with 15 amp circuits however it is seldom done that way. If you use 15 amps in a kitchen then you have to split wire the device and have 2- circuits to the receptacle.

A comment from a Canadian


Yup, split wire the kitchen, 15 amp everything else. That was the norm up until 10 years ago.

20 amps is popping up today because of GFCI protection and the CEC trying to hard to harmonize with the NEC.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
Voltage drop and lamp flicker is also a consideration. #14 AWG and 15 A circuits should go away entirely, IMO. It' not that they don't "work", it's just not that much more expensive to go up to #12 and it wouldn't make any sense to put a 15 A breaker on a #12 circuit. I don't know why Canadian code is different in this aspect. But I have little interest in re-writing the NEC for non-safety-related issues. And if I did, this would be way down on my list.

If we were starting from scratch, we should make 240 V the standard for all branch circuits. That would be a battle worth fighting.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
Some very eye opening parallels , as well as differences exist betwixt CEC & NEC
I wish this forum would have more Canadian sparks, and embrace those differences
I'll wager some rather educational

~RJ~
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Voltage drop and lamp flicker is also a consideration. #14 AWG and 15 A circuits should go away entirely, IMO. It' not that they don't "work", it's just not that much more expensive to go up to #12 and it wouldn't make any sense to put a 15 A breaker on a #12 circuit. I don't know why Canadian code is different in this aspect. But I have little interest in re-writing the NEC for non-safety-related issues. And if I did, this would be way down on my list.

If we were starting from scratch, we should make 240 V the standard for all branch circuits. That would be a battle worth fighting.


Flickr is a design issue in that a seperate circuit can mitigate that. Voltage drop with 20 amps on #12 vs 15 amps on #14 is about the same. If you ever worked with #12 in pancake boxes and high hats you would wish #14 was run.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
I'm still a 20a receptacle/15a lighting kinda guy.
Back in about 1999 I wired a community poolhouse that way, not realizing it was considered a commercial space. Inspector saw the #14 and was gonna fail it, then he saw me and said he thought it looked like my work. Asked me if I had any receptacles on 15 amp circuits, and I told him no. Only the lighting. So he passed it.

For ease of installation, I have always preferred #14 as much as possible, but I'm gravitating more toward using #12 on all receptacles
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Back in about 1999 I wired a community poolhouse that way, not realizing it was considered a commercial space. Inspector saw the #14 and was gonna fail it, then he saw me and said he thought it looked like my work. Asked me if I had any receptacles on 15 amp circuits, and I told him no. Only the lighting. So he passed it.

For ease of installation, I have always preferred #14 as much as possible, but I'm gravitating more toward using #12 on all receptacles
Why would he fail receptacles on 15 amp circuits?
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Why would he fail receptacles on 15 amp circuits?
it's such a common practice here to wire everything commercial on minimum 20 amp circuits, nobody even thinks twice about it. Even though it's not an NEC requirement, that would be beyond sacrilegious. That would be akin to a mortal sin.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
it's such a common practice here to wire everything commercial on minimum 20 amp circuits, nobody even thinks twice about it. Even though it's not an NEC requirement, that would be beyond sacrilegious. That would be akin to a mortal sin.
LOL. :LOL:
 

Frank Licata

Member
Location
Massachusetts
Occupation
Electrical Contractor
Why does the code require 20 amp circuits when in Canada 15 amp circuits are the norm for everything?
20a for commercial. 15a and 20a for residential depending on where in the house. Practically speaking, it's usually more economical to go 20a everywhere in the house because of the cost of AFCI/GFCI circuit breakers. That way you can do more with the larger circuit, and have less circuits.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
20a for commercial. 15a and 20a for residential depending on where in the house. Practically speaking, it's usually more economical to go 20a everywhere in the house because of the cost of AFCI/GFCI circuit breakers. That way you can do more with the larger circuit, and have less circuits.
Do you mean that using 20 amp general branch circuits allows you to add more lights to each circuit therefore using less circuits?

Welcome to the Forum. :)
 

Frank Licata

Member
Location
Massachusetts
Occupation
Electrical Contractor
Do you mean that using 20 amp general branch circuits allows you to add more lights to each circuit therefore using less circuits?

Welcome to the Forum. :)
Yes, thats what I mean. You can pickup more outlets with a 20a circ than with a 15a circ, which means less circuits and less AFCI circuit breakers. The cost difference between #12 and #14 wire is not as bad as the breaker cost. Personally, the only #14 that I would use in a house is 14-3 for the smoke/co detectors.
 