wwhitney
- Berkeley, CA
- Retired
Just curious--what code section would require that the switch be in the branch circuit wiring, rather than the fixture wire?Where the switch supplies a single lighting outlet, I think you can make a case for using fixture wire as a tap to the lighting outlet, with the tap originating at the load side of the switch.
But for the OP, the insulation types in Table 402.3 Fixture Wire do not overlap with the insulation types in Table 310.4 on branch circuit wiring. So if the OP has #14 building wire, rather than fixture wire, 240.5(B)(2) would not apply.
Cheers, Wayne