20 amp lighting circuit?

Status
Not open for further replies.

frankft2000

Senior Member
Location
Maine
I have read that the NEC requires that all lighting ciruits be 15 amp, but I can't seem to find it in the code. Is it there?
 
Re: 20 amp lighting circuit?

But you are limited to a load of 16 amps on a 20 amp circuit since lighting is considered a continous load.

Maybe thats what you were thinking of.


Steve
 
Re: 20 amp lighting circuit?

Originally posted by steve66:
But you are limited to a load of 16 amps on a 20 amp circuit since lighting is considered a continous load.
Technically, I don't believe lighting is always considered to be continuous, but it's still good practice to assume it is and load your circuits accordingly.

I use 20A circuits for lighting, but I always limit the max load to 16A.
 
Re: 20 amp lighting circuit?

if it is residential 15 or 20 is legal and i prefer 15 due to some lamp cords being under 18 gage .This is just personal choice but NEC allows 15 or 20
i also would not go past 80 % load
Must ask if you read it in nec why are you asking ? :confused:

[ July 12, 2004, 09:18 PM: Message edited by: jimwalker ]
 
Re: 20 amp lighting circuit?

240.5(B)(1) allows 18 AWG lamp and appliance cords to be plugged into 20 amp branch circuits.
 