Can you tell me if NEC allows a 20 amp rated switch to be tapped of a 60 amp riser feeder and then to a 20 amp fuse holder then to a FCU? This will all occur within 10' of the tap.
 
Re: 20 amp rated switch tapped off a 60 amp riser feed

I'm guessing Fan Coil Unit.
 
Re: 20 amp rated switch tapped off a 60 amp riser feed

Are you talking about type S plug fuses or class G fuses? For ordinary cartridge fuses you have a problem with somebody sticking in a larger fuse such as hooking up a second load.
 
Re: 20 amp rated switch tapped off a 60 amp riser feed

Actually it would be a small glass fuse or something of this type. It would have to rated for 300 volts. You know, a small tube type fuse in a turn in holder.
 
Re: 20 amp rated switch tapped off a 60 amp riser feed

My real question is would the switch be permisble as a 20 amp rated switch, even though it is a 60 amp protected circuit? It would be cost prohibitive to try to install a 60 amp rated switch.
 
Re: 20 amp rated switch tapped off a 60 amp riser feed

I think so. The tap conductors are reverse protected, the switch would be protected by the same principle.