so far i havnt been able to locate an exception for "not" doing this. Is it safe to use a 3 phase breaker for a 220/20 amp outlet - (a/b phase). and also use the c phase on the same breaker for the 120v 20 amp outlet? both circuits with a dedicated neutral.
 
Welcome to the forum.:)

I have moved this post to it's own thead so it doesn't hyjack the original thread as well as providing more views.

Chris
 
Seems fine to me as long as you don't mind both loads going off at the same time for maintenance or if one trips.
 
I agree with Rob. Not a good design, because of maintenance constraints, but not unsafe, and not a code violation.

Welcome to the forum.
 
could an inspector claim 110 due to the common use for a 3pole breaker is for a 3pole equipment?
 