200.2[(A)] grounded insulation

Status
Not open for further replies.

fmtjfw

Senior Member
Anybody know why 200.2[(A)] requires the grounded conductor to be insulated for the circuit voltage for 0--1000V, but only 600V for 1001V and over? Is there something special about 601--1000V?
 

Attachments

  • 200.pdf
    13.9 KB · Views: 0

jcormack

Member
Location
Pennsylvania
Most higher voltage power conductors have an over all-shield (braid or tape) within the cable that is grounded, no real need for higher voltage insulation on the ground wire
 