Hi folks,
I believe I know the correct answer but would appreciate your professional comments. A 200 amp service is run into a 100 amp rated panel and main breaker. The 100 amp breaker is going to limit the amperage going out of the panel, however the panel is only rated for 100amps. Can #4 aluminum fit into a 100 amp breaker? It appeared it must have been drilled out, but I couldn't tell for certain with the anti-oxidant paste present.
The 100 amp panel is full. My recommendation will be to have a qualified electrician evaluate and repair / replace as needed. They should change out the panel to a 200 amp panel citing the panel is not rated for 200amps and possible manipulation to the main lug area. By changing to a 200 amp panel it will be adding capacity to the dwelling if needed in the future.
However the homeowner selling the home may see it as just fine.
I believe I know the correct answer but would appreciate your professional comments. A 200 amp service is run into a 100 amp rated panel and main breaker. The 100 amp breaker is going to limit the amperage going out of the panel, however the panel is only rated for 100amps. Can #4 aluminum fit into a 100 amp breaker? It appeared it must have been drilled out, but I couldn't tell for certain with the anti-oxidant paste present.
The 100 amp panel is full. My recommendation will be to have a qualified electrician evaluate and repair / replace as needed. They should change out the panel to a 200 amp panel citing the panel is not rated for 200amps and possible manipulation to the main lug area. By changing to a 200 amp panel it will be adding capacity to the dwelling if needed in the future.
However the homeowner selling the home may see it as just fine.