200 amp panel and main breaker with 100 amp service

729Zoom

Member
Location
Los Angeles
Occupation
Retired
I have 100 amp service from the utility pole and had an emergency repair on my 45 year old 100 amp panel when a bus bar went bad. My electrician advised me to get a 200 amp solar panel so I would not need to change the panel again if I decided to upgrade. The panel has all 200 amp wiring and a 200 amp main breaker. He claims it is not a code violation to have a 200 amp main breaker with a 100 amp service (with small wires that I am sure are not even rated for 100 amps) but I read he should have used a 100 amp main breaker. He laughs at me and says "I don't know where you get this" when I told him I read it was a serious code violation and safety hazard. Is he right or do I need to demand he change the breaker to 100 amps?
 
More info is needed but if they left the 100 amp service conductors and changed the original OCPD from 100 to 200 then there is a violation of 230.90(A).

230.90(A) Ungrounded Conductor.
Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the ampacity of the conductor
 
Meter main installs typically dont have service entrance conductors, so a 200A one would be OK. I you have separate conductors from meter to panel, those need to be rated 200A (or within 200A round up) if landed in a 200A main.
 