I need to design 120/240v single phase service for part of a Children's Village in Brazil. It's for Rio street kids. That would be 5 houses now, and 2 in the future. Two of the homes would have runs of 210 feet and the others 125-150 feet. Each house will have a 100 amp panelboard. I will propose the power co. mount a 50kva transformer pole and one meter. The power co. will run the transformer's secondary to their junction box just below the transformer. I will tie into this secondary buss-junction box with my secondary cables and run down the pole, and enter the top of a 200 amp outdoor panelboard positioned adjacent to the pole. Need to build a trough at the bottom of this 200 panel to support the cables as they leave the panel to the houses. Can I use 7-black 60 amp breakers in that 200 amp panel to serve the home's 100 amp panels? Plan on exiting the bottom of the trough with conduit, but then DB the runs to each house. Would it be better to install 60 amp disconnect switches on a rack at the base of the pole instead of the 200 amp panel? If so, please be specfic, thanks. Oh, and if this is okay by NEC any suggestions re: cable size, conduits, etc. would be appreciated. Unfortunaelty I did not get to meet with the power co. on my visit there. You must submit your plans to them first. Thanks!!!