beachshadow
Member
- Location
- Cobb County
- Occupation
- Electrical Contractor
SquareD has been putting that on all of there Combination Service Entrance Devices for a while.Why does the sticker say Emergency Disconnect? Are you under the 2020 NEC? Looks like you have a 150 amp service disconnect.
It's actually a meter/main so the service disconnect is the 150 circuit breaker because it's connect directly to the meter by the factory conductors that aren't visible.Looks to me like the service conductors hit the ats first, thus a 230.90 violation if the SE conductors are 150A (#1 CU or 2/0 AL)
If ATS was installed in front of the existing main (service side) then yes it must become the main, and be service rated. But the photos looks like a meter/main, thus the ATS should be a non service rated ATS (yes, generac makes this animal) and installed in what appears to be the proper wireing configuration.This installation failed inspection. Inspector said the ATS panel had to become the service main and have breaker changed to 150A. So, what is the specific NEC Code that does not allow my installation?
I agree if conductors are sized to the overcurrent protection provided by the meter/main no problem with that even if the ATS rated to a higher amperage.If there is a 150 amp service disconnect with a 200 amp ATS and 150 amp protected conductors what is the violation?
Generac has within there listing instructions for connecting the ATS directly to the Utility. So, consider the context of the statement within their "listing" that quoted. Because it was stated within the context of instructions for connecting directly to the Utility. Please notice within the same set instructions for connecting the ATS directly to the utility. That it also says, "Neutral to Ground jumper wire is provided use if required by code."I agree if conductors are sized to the overcurrent protection provided by the meter/main no problem with that even if the ATS rated to a higher amperage.
My only question would be the use of a service rated ATS in a location permitting a non service rated ATS. Generac has within their "listing" that the bonding "not to be removed" on the service rated ATS, thus making it a "technical violation" IF this one is a service rated ATS.
Not sure what safety concern there is in the use of service rated one vs the other might be if all conductors are protected at an appropriately rated device though. We do it all the time with main breaker service rated panels used as a non service sub panel by just removing the bonding.
It's actually a meter/main so the service disconnect is the 150 circuit breaker because it's connect directly to the meter by the factory conductors that aren't visible.
An inspector actually said that? What could he possibly base that request on?Conclusion. I talked to the inspector. The installation was done correctly. He clarified his intentions. The correction is to put a locking means on the meter combo. This would prevent someone from changing the 150A main disconnect to a higher breaker size.
I guess I better start putting a locking means on all my panels and fused discos so no one can change an OCPD to a larger size.....An inspector actually said that? What could he possibly base that request on?
I’ve had them wanting “max fuse” on disconnects, but never on a breaker. He probably figured out he was wrong, and to save face, required the lock.Conclusion. I talked to the inspector. The installation was done correctly. He clarified his intentions. The correction is to put a locking means on the meter combo. This would prevent someone from changing the 150A main disconnect to a higher breaker size.