In GA it has to be at least 2" rigid metal for a service mast per the blue book. Don't know about your area, but I doubt PVC will be allowed.
 
Georgia Power is kinda weird sometimes, but as long as it is not supporting any of the drops (phone, cable, power, etc.) it is legal by code, but as @Sea Nile posted, it would be up to the poco to accept. Definitely would be tough trying to run that in rigid. Without a one shot bender, you would probably have to come straight down, turn a 90 at the meter level, and go across to the meter.
 