200 amp sub panel

Status
Not open for further replies.

packersbay

Member
Location
New mexico
Occupation
Electrician
So I am trying to fix a situation that some other contractor did, I have a indoor 200 amp sub panel that someone installed off of a what looks like a 100amp main service. I am going to install a new main 200amp service with panel being a feed thru 8 space outdoor. I want to feed the indoor panel from the feed thru lugs. the distance is about max 15ft. I want to go thru attic with feeders to sub panel, so my question is what type of wire will be better for this and if it has to be in conduit.
 

acin

Senior Member
Location
pacific grove california
Occupation
general building contractor est.1984 . C 10 elec. lic.as of 8 / 7/ 2020
I was looking at 338.2 ,se cable has moisture resistant covering . Is that allowed in a wet location?
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Please forgive my ignorance here but I have some questions :
  1. Is the sub-panel a MBP or a MLO panel (not that it matters either way)?
  2. If you are feeding off a set of feed-thru lugs wouldn’t the sub-panel be considered service equipment?
  3. Would you have to separate the EGC’s from the neutrals?
  4. If you are going to use 4\0, 4\0, 4\0, 2 SER cable will you have lugs to land it on in the New 200A MB panel?
You do not need to sleeve the SER cable in conduit unless you have a local ordinance that requires it.
  1. How do you plan to bend the cable thru the LB?
 

kwired

Electron manager
Location
NE Nebraska
So I am trying to fix a situation that some other contractor did, I have a indoor 200 amp sub panel that someone installed off of a what looks like a 100amp main service. I am going to install a new main 200amp service with panel being a feed thru 8 space outdoor. I want to feed the indoor panel from the feed thru lugs. the distance is about max 15ft. I want to go thru attic with feeders to sub panel, so my question is what type of wire will be better for this and if it has to be in conduit.
That in itself is not a problem unless the load exceeds the 100 amp feeder breaker.

If the load is not there or is not anticipated to be there with any proposed additions I wouldn't call this something that needs attention, presuming it otherwise meets code requirements.

If the existing 100 amp service is in need of replacement I would probably replace with 200 amp though. Could possibly even then still put the feeder on a 100 amp breaker in said 8 space outdoor panel if the load isn't there.

Just some thoughts, you do what you feel is best.
 

packersbay

Member
Location
New mexico
Occupation
Electrician
Please forgive my ignorance here but I have some questions :
  1. Is the sub-panel a MBP or a MLO panel (not that it matters either way)?
  2. If you are feeding off a set of feed-thru lugs wouldn’t the sub-panel be considered service equipment?
  3. Would you have to separate the EGC’s from the neutrals?
  4. If you are going to use 4\0, 4\0, 4\0, 2 SER cable will you have lugs to land it on in the New 200A MB panel?
You do not need to sleeve the SER cable in conduit unless you have a local ordinance that requires it.
  1. How do you plan to bend the cable thru the LB?
The sub-panel is a 200amp main breaker, Yes we would separate EGC’s in sub-panel. In order for us to get SER cable from exterior to interior we would have to use conduit to penetrate to attic then run cable to sub in attic
 

packersbay

Member
Location
New mexico
Occupation
Electrician
That’s right, I’ll probably not use a LB and just go straight up under eave of house and it will eliminate trying to bend wire
 

acin

Senior Member
Location
pacific grove california
Occupation
general building contractor est.1984 . C 10 elec. lic.as of 8 / 7/ 2020
Are the utility conductors over head or ug? The feed through lugs on our meter main combo are on the bottom with oh drop
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Hell ya that is hard. I use a 3" LB on 2" pipe if I have to do that for the extra room. You must work out!
If you're only sleeving up in?
Or if you're sleeving down and in?

You curve the SER through the LB first, then straighten it and sleeve the pipe onto it. Pretty easy
 