infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 28, 2011 #21 Sierrasparky said: Lots of moots going on here :blink: Click to expand... LOL, have there been others?
Sierrasparky said: Lots of moots going on here :blink: Click to expand... LOL, have there been others?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jun 28, 2011 #22 I agree with trevor. 3/0 is fine and installed on a 200 amp breaker. No derating needed.