200 Amp Wire Size for MA

Status
Not open for further replies.

Needle

Member
Location
Massachusetts
Occupation
Retired
Perhaps I've been out of it for too long, but it was my understanding that you can still use 4/0, 4/0, 2/0 AL Triplex cable in 2' PVC for a service feed to the Meter/Disconnect. With that stated, wouldn't this transform into similar conductor sizes for feeding the main panel and include a EGC with these three, via a four wire cable. All I am finding for SE or SER is 4/0, 4/0, 4/0, 2/0 AL. Please advise. Thanks all
 
Last edited:
Try you local supply house.
Big box stores carry what you're seeing but an electrical supply store should carry what you're looking for.
 
Thanks for the advice. I was actually looking for clarity on the actual wire sizes.
4/0 Al is typical for 200amp service.
As for the neutral, I would get it full sized 4/0AL as well unless a load calculation was performed and maximum neutral current was calculated.
 
You can even fit 4/0-4/0-4/0-2/0 in 2" PVC. I prefer stripping the sheath of SE and SER.

I usually remove the bare from SER and use the insulated neutral in conduit.
 
The neutral can be as small as #2 if you do a load Calc. Most use 2/0, typically there is minimal unbalanced current. The egc size is sized for the 200 amp ocpd
 
Thanks guys. I was thinking of using the standard 4/0, 4/0, 2/0 triplex from weatherhead down to the meter/disconnect. I wanted to add an EGC from the meter/disconnect to the main, now sub panel. That combination of wire(SE/SER) is just difficult to locate. Is my sizing correct?
 
Thanks guys. I was thinking of using the standard 4/0, 4/0, 2/0 triplex from weatherhead down to the meter/disconnect. I wanted to add an EGC from the meter/disconnect to the main, now sub panel. That combination of wire(SE/SER) is just difficult to locate. Is my sizing correct?
4/0, 4/0, 2/0, w/4 grnd
 
Thanks Curt
That’s what I am finding. I just find it odd that you can find 4/0, 4/0. 2/0 triplex for the line side of the meter but you can only find 4/0 neutral for the load side. Why is that
 
Your not going to find SER cable with a reduced "white wire" It will have 3-4/0 insulated wires and a 2/0 bare.
I'm finding that out.
It's been a long time since I bought any 4 conductor SE so maybe I didn't even get what I wanted then. I don't remember.....
It just seems silly to have a full sized neutral and a way oversized EGC for a 200 amp sub-panel feed.
 
I agree
What do you normally bring in from the meter disconnect?
3 wire with no EGC or 4 wire?
I’m trying to complete the path from the two ground rods through to the main panel
Water main is plastic so there is a galvanized pipe next to the water main that I bug onto and then the water pipe, then to the main panel. Just seems like overkill
Do I actually need the EGC from the main panel if I have all that inside?
Thanks
 
Thanks for the clarity. I appreciate it
It relates to the 2020 code for sure.
Just seems odd you need a 4/0 EGC from the meter/disconnect
 