lendog
Member
- Location
- California
I have a question when you have a single phase 200 amp panel is each phase on the panel good for 100 amps and thats how you get 200, or is each phase good for 200 amps?
lendog said:I have a question when you have a single phase 200 amp panel is each phase on the panel good for 100 amps and thats how you get 200, or is each phase good for 200 amps?
iwire said:Each phase is capable of 200 amps.
But amps (current) is a poor way to describe how much power a panel is capable of providing.
If you are really interested in how much power a panel can provide you should be thinking in terms of watts or actually Kilowatts (KW).
I will use a 200 amp panel as an example.
A 200 amp 120/240 single phase panel in a home is capable of providing 48,000 watts (48 KW) of power.
A 200 amp 208Y/120 three phase panel is capable of providing 71,000 watts (71 KW) of power.
A 200 amp 480Y/277 three phase panel is capable of providing 166,000 watts (166 KW) of power.
As you can see three 200 amp panels can have greatly different power capabilities.
Dexie123 said:I'm with you Iwire but if you are saying "each phase" is capable then w'hy wouldn't you multiply, in say your first example, 240v * 400 to give you 96kw as apposed to 240v * 200 giving you 48kw?
1 phase 120 v x 200 a = 24000 + 120v x 200 a = 24000 = total 48 kvaDexie123 said:I'm with you Iwire but if you are saying "each phase" is capable then w'hy wouldn't you multiply, in say your first example, 240v * 400 to give you 96kw as apposed to 240v * 200 giving you 48kw?
busman said:Is there really an "electrician" who doesn't know how many amps/phase in a residential 200A service. The OCPD should tell you that. Sounds like Harry-Home-Owner?
Sorry - just grumpy tonight.
Mark
No, you're wrong. 200a A to N is 200a @ 120v, or 24Kva; 200a B to N is 200a @ 120v, or 24Kva. Add the two together and you get 200a A to B, which is 48Kva.cjnickjr said:First, each phase is capable of 200A whether the current is line to line or line to neutral. You would'nt put a 200A load from A to Neutral and an additional 200A load from B to Neutal. Thats 400 amps, alot of fire and smoke.
LarryFine said:No, you're wrong. 200a A to N is 200a @ 120v, or 24Kva; 200a B to N is 200a @ 120v, or 24Kva. Add the two together and you get 200a A to B, which is 48Kva.
Or, you can do 200a A to B, which is 48Kva. You can do one or the other, or a mix, such as 100a A to N and 100a B to N and 100a A to B all at the same time.
You can load A to N at 200a, and then as you add load to B to N, each amp added is an amp less on the neutral, until you have 200a on A and B, and zero amps on the neutral.
cjnickjr said:Let me take a shot at this.
First, each phase is capable of 200A whether the current is line to line or line to neutral.
cjnickjr said:You would'nt put a 200A load from A to Neutral and an additional 200A load from B to Neutal. Thats 400 amps, alot of fire and smoke.
cjnickjr said:Second, what would you calculate for a 3 phase Delta 240/120V panel?
(3phase 120V x 200A = 24000 x 3ph = total 72kva?) Although your other calculations came out as correct the formula used was not. The correct calculation in this case is 240V x 200A x 1.73 = 83KVA. Compare this to 208V x 200A x 1.73 = 72KVA
LarryFine said:No, you're wrong. 200a A to N is 200a @ 120v, or 24Kva; 200a B to N is 200a @ 120v, or 24Kva. Add the two together and you get 200a A to B, which is 48Kva.
Or, you can do 200a A to B, which is 48Kva. You can do one or the other, or a mix, such as 100a A to N and 100a B to N and 100a A to B all at the same time.
You can load A to N at 200a, and then as you add load to B to N, each amp added is an amp less on the neutral, until you have 200a on A and B, and zero amps on the neutral
jaylectricity said:What good would it do Harry-Home-Owner to know the answer to this question? Sounds like a guy just getting into the trade asking a question that he didn't feel comfortable asking his real life peers.
Take a chill pill, tonight will be over soon enough and then it will be MONDAY!
busman said:OK - now it's Monday morning. Sorry - at least I knew enough to apologize yesterday as soon as I typed it. It just seemed like a fairly basic question from a new member on the first post with a profile that says "electrician".
I was grumpy because I spent most of the weekend doing the low-belly-crawl thru bad yellow insulation in a 120 degree attic to clean up behind a HHO who didn't use boxes (just attach light, recpt, etc. to plaster); didn't use wirenuts (just make two hooks and tape with duct tape); didn't know they made 3-wire cables so just taped single conductors to 2-wire cables. Needless to say, this eventually started a fire. Was just having a low tolerance day. I would post the photos, if I could ever figure out how.
Mark
Mark, if you like, email me the photos and I'll put them on my server and post links.busman said:I would post the photos, if I could ever figure out how.