- Illinois
- retired electrician
I still don't understand how a 3 phase load puts current on the neutral.That's where the neutral was connected.
The harmonics are fed into the neutral.I still don't understand how a 3 phase load puts current on the neutral.
Just to the neutral. The first harmonic is the 5th, not third.1) If you had a pure third harmonic load, no net power would be delivered to the load.
Say you have a perfect sine voltage source connected to a bizarre load that draws perfect 3rd harmonic current. Because of the orthogonality of sine functions the integral of voltage * current would be zero, no power delivered.
2) If a load has no connection to the neutral it can't inject harmonics on the neutral.
A large three phase rectifier with no neutral connection could not draw any third harmonic current.
I could imagine some topologies where a drive had a neutral connection.
Beo: could you explain how these particular drives were connected to the neutral?
Jon
Then maybe I am wrong. We definitely used harmonic filters.5th harmonic is not a zero sequence and doesn't add on the neutral.
Thanks
Jon
Even though they do not cause neutral current, non-triplet harmonics are still consdiered objectionable when they cause current harmonics to POCO or voltage harmonics on other loads. Hence the need for filtering.Then maybe I am wrong. We definitely used harmonic filters.
Exactly.Even though they do not cause neutral current, non-triplet harmonics are still consdiered objectionable when they cause current harmonics to POCO or voltage harmonics on other loads. Hence the need for filtering.