2002 article in "Fire & Arson Investigator" about thermally insulated NM cable
According to authors Goodson, Perryman, and Colwell, they investigated a house fire and found thermally damaged NM cable embedded in polyurethane foam insulation. They then set up a test rig and reported alarmingly high temperatures, enough to degrade electrical insulation, on foam-embedded cables carrying a prolonged 100% of maximum rated load. That's not a realistic test, of course, but if the circuit breaker permits it then it needs to be provably safe.
Fire & Arson Investigator magazine, July 2002, online at http://goodsonengineering.com/wp-co...yurethane-Foam-Systems-on-Wiring-Ampacity.pdf
Is anyone seeing problems in the field with NM cable in older houses that's been buried under retrofitted insulation, also including blown-in cellulose? It's a pretty common situation and if there's a real issue there should be lots of incident reports by now.
There have been some related discussions on this forum:
http://forums.mikeholt.com/showthread.php?t=120134
http://forums.mikeholt.com/showthread.php?t=121136
The NEC requires derating if multiple cables are bundled together or crammed through an insulated hole together. If the 2002 article is right, then that's not adequate.
It may not be right. There's an NEMA publication, based on a University of Toronto study, which reports utterly reasonable temperatures for heavily loaded conductors in thermal insulation:
https://www.nema.org/Technical/Docu...NM Cable encased in spray-foam insulation.pdf
Besides, the reported temperatures in their control group of conductors in free air seem strange.
On the other hand, I can't find the University of Toronto study and it's hard to argue with a building that's caught fire.
What are people's professional opinions about whether there's a real issue? Has there been any additional lab work since? Do tests of suitability for "insulation contact" already include completely surrounding the cable by deep thermal insulation?
According to authors Goodson, Perryman, and Colwell, they investigated a house fire and found thermally damaged NM cable embedded in polyurethane foam insulation. They then set up a test rig and reported alarmingly high temperatures, enough to degrade electrical insulation, on foam-embedded cables carrying a prolonged 100% of maximum rated load. That's not a realistic test, of course, but if the circuit breaker permits it then it needs to be provably safe.
Fire & Arson Investigator magazine, July 2002, online at http://goodsonengineering.com/wp-co...yurethane-Foam-Systems-on-Wiring-Ampacity.pdf
Is anyone seeing problems in the field with NM cable in older houses that's been buried under retrofitted insulation, also including blown-in cellulose? It's a pretty common situation and if there's a real issue there should be lots of incident reports by now.
There have been some related discussions on this forum:
http://forums.mikeholt.com/showthread.php?t=120134
http://forums.mikeholt.com/showthread.php?t=121136
The NEC requires derating if multiple cables are bundled together or crammed through an insulated hole together. If the 2002 article is right, then that's not adequate.
It may not be right. There's an NEMA publication, based on a University of Toronto study, which reports utterly reasonable temperatures for heavily loaded conductors in thermal insulation:
https://www.nema.org/Technical/Docu...NM Cable encased in spray-foam insulation.pdf
Besides, the reported temperatures in their control group of conductors in free air seem strange.
On the other hand, I can't find the University of Toronto study and it's hard to argue with a building that's caught fire.
What are people's professional opinions about whether there's a real issue? Has there been any additional lab work since? Do tests of suitability for "insulation contact" already include completely surrounding the cable by deep thermal insulation?