Re: 2005 Grounding Electrode system
Dave,
I don't agree. If there is 20' of rebar in the bottom of a footing that is in direct contact with the earth in a new building, that rebar must be used because it is "present". Just because you choose to add copper to the footing, does not make the rebar go away. If it is there, you are required under the 2005 wording to use it.
Don
Dave,
I don't agree. If there is 20' of rebar in the bottom of a footing that is in direct contact with the earth in a new building, that rebar must be used because it is "present". Just because you choose to add copper to the footing, does not make the rebar go away. If it is there, you are required under the 2005 wording to use it.
Don