construct
Senior Member
- Location
- Branson, Missouri
This requires receptacle outlets to be located above, but not more than 20" above the countertop. Exception to (5): To comply with conditions in (1) or (2), you shall be permitted mount them no more than 12" below the countertop unless the top extends more than 6" beyond it's base. So this means if I can't put them below because of the countertop extension, then I must put them in the backsplash for an island and in the wall or bottom of upper cabinet, no more than 20" above for wall counter spaces. Then, further in Exception to (5), (2)says: On island and peninsular countertops where the countertop is flat across it's entire surfaceand there are no means to mount one within 20" above, then I am not required to have a receptacle(s) on this type of island or peninsula.
This is my take on the requirement.
(Sorry for the lengthy text)
It has been a topic of debate among electricians and inspectors in our area for a while.
I would appreciate hearing different opinions.:roll:
This is my take on the requirement.
(Sorry for the lengthy text)
It has been a topic of debate among electricians and inspectors in our area for a while.
I would appreciate hearing different opinions.:roll: