Have to run 120/240 vac feeder, 4 wire, (3) 2/0 w/#6cu from 200a main disco
(outside) to breaker panel for manuf. home. It is a 65' run under the home to the panel. (no slab, just frost piers) Can I direct bury or does it all (other than conduit stub to protect the wire) have to be in conduit (THWN). I am confused by "outside of the building".