From the 2005:
Could someone clarify for me whether the motor is to be bonded under the 2005? Here is the ROC substantiation:
As I'm sure you will notice, this is a substantial cahnge in wording from the 2002 NEC, which specifically references the motor. I am having a bit of a difficult time fully understanding the ROC comment of the submiiter. I have never claimed to be the expert on voltage gradients, but reading the substantiation, it seems as though UL (and the CMP) are of the opinion that a motor (double insulatd or not) will not create a voltage gradient.680.74 Bonding. All metal piping systems and all grounded metal parts in contact
with the circulating water shall be bonded together using a copper bonding
jumper, insulated, covered, or bare, not smaller than 8 AWG solid.
And the panel statement:Recommendation: The Panel Statement regarding the rejection of proposal
17-152 indicated they believed a double insulated whirlpool bath pump provided
an increased level of safety. Although this is the case for above ground
storable and non-storable swimming pool pumps, I believe it is not the case
with whirlpool baths utilizing double insulated pumps. The pump designs and
their installations are different.
Whirlpool bath pumps are not accessible by the bathtub occupants and are
required by UL 1795 to have their live parts above the mounting service in the
event of a leak. They are also required to have their internal metal parts that
might become energized in a failure (the motor shaft in particular) isolated
from the water. An internal failure of the motor would not produce the same
hazards as an outdoor storable pool unit that is accessible and may have wet
surfaces. The grounding of internal dead metal parts, therefore, is not needed.
Due to the requirements on the double insulated bathtub pumps and their
mounting in UL 1795, the text from 680.74, ?and providing a means for
grounding internal nonaccessible, non-current carrying metal parts? should,
therefore, be deleted.
Substantiation: Present text requires substantial modification of the pump
motor without an overall increase in the safety of the complete whirlpool bath.
Panel Meeting Action: Accept in Principle
Panel Statement: The need for bonding in a bathroom differs from the need
for bonding in a pool area. Electrical equipment of a hydromassage bathtub is
not accessible to users of the tub. Only parts that can cause a voltage gradient
in the bathtub need to be bonded. Section 680.74 has been concisely reworded
to require the bonding of only the parts that present a risk of creating voltage
gradients in the hydromassage bathtub. The panelʼs action on 17-183 supersedes
the panelʼs action on ROP 17-153.
Number Eligible to Vote: 10
Ballot Results: Affirmative: 10