M_J_C
Member
- Location
- Southeast Florida
The 2007 Florida Building Code incorporates the IRC 2006 code (R313.1 Smoke detection and notification), which requires the following:
"Household fire alarm systems installed in accordance with NFPA 72 that include smoke alarms, or a combination of smoke detector and audible notification device installed as required by this section for smoke alarms, shall be permitted. The household fire alarm system shall provide the same level of smoke detection and alarm as required by this section for smoke alarms in the event the fire alarm panel is removed or the system is not connected to a central station."
My dilemma is this, many homes require more than 12 smoke detectors to meet the 2007 NFPA 72 requirements. We know that 12 Smoke detectors is the interconnected limit for a non-supervised loop (11.8.2.2 (1)). The solution has been to install a supervised system, which will allow 42 smoke detectors (11.8.2.2 (3)). The problem is that the supervised system has to have a panel, which if removed (as stated by IRC/FBC R313.1) would render the system useless.
I have not been able to find a "supervised" system that does not have a system panel, does anyone know of a work around?
By the way, the 2009 IRC eliminated this requirement, probably because of this very issue. No hardware exists (to my knowledge) that will meet this requirement. I have inquiries to suppliers and manufacturers, but no one has a solution. I have contacted a very helpful person at the FBC office, who has 30 years in the trade, he can plainly see the problem but his only answer was to shake the tree, which is what I am doing now. The problem with this approach is that it will take Florida a couple of years to update the code (2011 code cycle?).
"Household fire alarm systems installed in accordance with NFPA 72 that include smoke alarms, or a combination of smoke detector and audible notification device installed as required by this section for smoke alarms, shall be permitted. The household fire alarm system shall provide the same level of smoke detection and alarm as required by this section for smoke alarms in the event the fire alarm panel is removed or the system is not connected to a central station."
My dilemma is this, many homes require more than 12 smoke detectors to meet the 2007 NFPA 72 requirements. We know that 12 Smoke detectors is the interconnected limit for a non-supervised loop (11.8.2.2 (1)). The solution has been to install a supervised system, which will allow 42 smoke detectors (11.8.2.2 (3)). The problem is that the supervised system has to have a panel, which if removed (as stated by IRC/FBC R313.1) would render the system useless.
I have not been able to find a "supervised" system that does not have a system panel, does anyone know of a work around?
By the way, the 2009 IRC eliminated this requirement, probably because of this very issue. No hardware exists (to my knowledge) that will meet this requirement. I have inquiries to suppliers and manufacturers, but no one has a solution. I have contacted a very helpful person at the FBC office, who has 30 years in the trade, he can plainly see the problem but his only answer was to shake the tree, which is what I am doing now. The problem with this approach is that it will take Florida a couple of years to update the code (2011 code cycle?).