There is one section in the 2008 NEC that will require the removal of abandoned line voltage conductors/wiring methods. Can you find it?
ryan_618 said:Can you find it?
640.6(C), but that's not line voltage... ditto for 645.5(F)ryan_618 said:There is one section in the 2008 NEC that will require the removal of abandoned line voltage conductors/wiring methods. Can you find it?
charlie b said:I heard a rumor to the effect that the State of Washington is considering not adopting the 2008 NEC at all, ever.
Chris, you're on the right track, sort of. It has nothing to do with Class 3 circuits, however.raider1 said:How about 725.25.
This requires that the abandonded portion of Class2, Class 3, and PLTC cables be removed or identified for future use.
Class 3 circuits can have voltages as high as 150 volts.
Chris
I already said that one... not line voltage I had presumed, since I was thinking Cat5.chris kennedy said:645.5(f)...
ryan_618 said:Well...you got it right...but you didn't know you got it right!