2008 Gfci

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
For the 2008 NEC requirement of GFCI within 6?-0? of a sink does this include the vertical as well as horizontal conditions?
 
Mike01 said:
For the 2008 NEC requirement of GFCI within 6?-0? of a sink does this include the vertical as well as horizontal conditions?


There is no exception such as with garages and basements where receptacles are not readily accessible, so I would do it. Probably depends on the AHJ....

Jim
 

electricmanscott

Senior Member
Location
Boston, MA
jimday said:
There is no exception such as with garages and basements where receptacles are not readily accessible, so I would do it. Probably depends on the AHJ....

Jim


That exception no longer exists.


GFCI protected within six feet of the sink regardless of height.
 

wirebender

Senior Member
Mike01 said:
For the 2008 NEC requirement of GFCI within 6?-0? of a sink does this include the vertical as well as horizontal conditions?

Yes, if it is within 6' of the outer edge of the sink. IMSO


jimday said:
There is no exception such as with garages and basements where receptacles are not readily accessible


Those exceptions were removed for the 2008 NEC.
 
Status
Not open for further replies.
Top