Here is how the 2008 NEC section will be reworded. I know it doesn't apply to the 2005 pool, but can be used as guidance for 2005 interpreatation. Notice the last statement made by the panel regarding WELDED WIRE MESH:
Panel Meeting Action: Accept in Principle
Revise as follows:
680.26 Equipotential Bonding.
(A) Performance. The equipotential bonding required by this section shall be installed to reduce voltage gradients in
the pool area.
(B) Bonded Parts. The parts specified in 680.26(B)(1) through (B)(7) shall be bonded together using solid copper conductors, insulated covered , or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with 250. 8. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to any remote panelboard , to service equipment, or electrodes.
(1) Conductive Pool Shells. Bonding to conductive pool shells shall be provided as specified in 680. 26(B)(1)(a) or 680.26(B)(1)(b). Poured concrete, pneumatically applied or sprayed concrete, and concrete block with painted or plastered coatings shall all be considered conductive materials due to water permeability and porosity. Vinyl liners
and fiberglass composite shells ar shall be considered to be non-conductive materials.
a. Structural Reinforcing Steel. Unencapsulated structural reinforcing steel shall be bonded together by steel tie wires or the equivalent. Where structural reinforcing steel. encapsulated in a nonconductive compound, a copper conductor arid shall be installed in accordance with;- 680.26(B)(1)(b).
b. Copper Conductor Grid. A copper conductor grid shall be provided and shall comply with the following conditions:
(1) Be constructed of minimum 8 AWG bare solid copper conductors bonded to each other at all points of
crossing.
(2) Conform to the contour of the pool and the pool deck.
(3) Be arranged in a 300 mm (12 in. ) by 300 mm (12 in.) network of conductors in a uniformly spaced
perpendicular grid pattern with a tolerance of 100 mm (4 in.)
(4) Be secured within or under the pool no more than 150 mm (6 in.) from the outer contour of the pool shell.
(2) Perimeter Surfaces. The perimeter surface 2b extends for 1 m (3 ft) horizontally beyond the inside walls of the pool:- and shall includes unpaved surfaces as well as poured concrete and other types of paving. Bonding to perimeter surfaces shall provided as specified in 680. 26(B)(2)(a) or 680.26(B)(2)(b), and shall be attached to the pool reinforcing steel or copper conductor grid at a minimum of four (4) points uniformly spaced around the perimeter of the pool. For non-conductive pool shells , bonding at four points shall not be required.
(a) Structural Reinforcing Steel. Structural reinforcing steel shall be bonded In accordance with 680.26 (B)(1)(a).
(b) Alternate Means. Where structural reinforcing steel is not available or is encapsulated in a nonconductive compound, copper conductor shall be utilized where the following conditions are met:
(1) At least one minimum 8 AWG bare solid copper conductors shall be provided.
(2) The conductor(sl shall follow the contour of the perimeter surface.
(3) Onlv listed splices shall be permitted.
(4) The required conductor shall be 450 to 600 mm (18 to 24 in.) from the inside walls of
the pool.
(5) The required conductor shall be secured within or under the perimeter surface 100 to 150 mm (4 to 6 in.) below
the subgrade.
(3) Metallc Components. All metallc parts of the pool structure , including reinforcing metal not addressed in 680.26(1)(a), shall be bonded. Where reinforcing steel is encapsulated with a nonconductive compound the reinforcinq steel shall not be required to be bonded.
(4) Underwater Lighting. All metal forming shells and mounting brackets of no-niche luminaires shall be bonded.
Exception: Listed low-voltage lighting systems with nonmetallic forming shells shall not requirejr bonding.
(5) Metal Fittings. All metal fittings within or attached to the pool structure shall be bonded. Isolated parts that are not over 100 mm (4 in.) in any dimension and do not penetrate into the pool structure more than 25 mm (1 in. ) shall not require bonding.
(6) Electrical Equipment. Metal parts of electrical equipment associated with the pool water circulating system including pump motors and metal parts of equipment associated with pool covers , including electric motors, shall be bonded.
Exception: Metal parts of listed equipment incorporating an approved system of double insulation shall not be bonded.
(a) Double-Insulated Water Pump Motors. Where a double-insulated water-pump motor is installed under the provisions of this rule , a solid 8 AWG copper conductor tt of sufficient length to make a bonding connection to a replacement motor shall be extended from the bonding grid to an accessible point in the mo vicinity of the pool pump motor. Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises , this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit.
(b) Pool Water Heaters. For pool water heaters rated at more than 50 amperes and having specific instructions regarding bonding and grounding, only those parts designated to be bonded shall be bonded and only those parts designated to be grounded shall be grounded.
(7) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways , metal piping, and all fixed metal parts shall be bonded.
Exception No. 1: Those separated from the pool by a permanent barrier shall not be reauired to be bonded.
Exception NO. 2: Those greater than (5 ft) horizontally of the inside walls of the pool shall not be reauired to be bonded.
Exception No. 3: Those greater than (12 ft) measured vertically above the maximum water level of the pool, or as measured vertically above any observation stands, towers, or platforms, or any diving structures shall not be required to be bonded.
Panel Statement: The revised text more clearly presents the requirements and meets the intent of the submitter.
The panel has removed the word " (rebar)" from 680.26(B)(1)a to clarify that welded wire mesh can be included in the term "structural reinforcing steel" where acceptable to the authority having jurisdiction.