I know there is a code change reguarding derating of SER and SEU except I can't find it.
Rick
Rick
I know there is a code change reguarding derating of SER and SEU except I can't find it.
Rick
Also take note of the change in terminology of main power feeder in regards to Table 310.15(B)(6).
Chris
Substanitive change. :smile:
This change has a wide sweeping effect in how the homes in my area are wired.
Chris
mikeames, If it is #2 Alum. ser and used indoors you have to use the 60deg. column for
ampacity, that would be 75 amps.
What if I was running it from my 100 amp main breaker disconnect to my indoor panel which contains all of my dwelling load?
Ok let me get this straight, 2/2/2/ Awg SER can be protected with a 100 OCPD when used as a feeder? I know that was the case years ago, and then there was a change and now its ok on 100? I have been putting it on 90. I guess I am ignorant. Opps.
Substanitive change. :smile:
I disagree.
There was no change, all they did was make the existing rule clearer. The intent and meaning has been the same for years.
Panel Statement: The panel agrees that the present wording is ambiguous. It is the panel?s intent that this allowance apply only to conductors carrying 100% of the dwelling unit?s diversified load.
Primarily how ?
iwire said:There was no change, all they did was make the existing rule clearer. The intent and meaning has been the same for years.