Tables 21-1 through 21-5 in the 2008 Soares book seem to support the conclusion that the values in Table 250.66 should be increased where the length of the grounding electrode conductor (GEC) exceeds 100 feet in length. This may or may not be true, but perhaps someone can help me clarify a few points.
1. Table 21-2 (column 4) shows the ampacity of the GEC to be based on the 75 degree column. Since this conductor is permitted to be bare, why limit the ampacity to the 75 degree column ?
2. Table 21-2 (asterick) tells us these values are based on the assumption that the GEC is the sole connection between the grounded system conductor and the electrode. What about the parallel path that consists of the grounded system conductor, the utility transformer, the grounding electrode at the transformer, and the earth. What about a third parallel path where a supplemental electrode is required?
3. Table 21.5 mysteriously arrives at two questionable conclusions. First, the voltage drop of the GEC, based on short-time current rating, should not exceed 40 volts. Why not 30 volts or 50 volts? Second, that the resistance of the GEC, when it exceeds 100 ft, should not exceed the resistance of 100 ft of the conductor specified in the table. Why not consider the total resistance of the path to ground where parallel paths exist?
4. Exactly what does the short-time current rating signify? Using the voltage drop formulas from the UGLY Book, I am unable to duplicate the author's voltage drop for the various conductors.
Thanks for your comments and
Happy New Year!
Brian Dolan
1. Table 21-2 (column 4) shows the ampacity of the GEC to be based on the 75 degree column. Since this conductor is permitted to be bare, why limit the ampacity to the 75 degree column ?
2. Table 21-2 (asterick) tells us these values are based on the assumption that the GEC is the sole connection between the grounded system conductor and the electrode. What about the parallel path that consists of the grounded system conductor, the utility transformer, the grounding electrode at the transformer, and the earth. What about a third parallel path where a supplemental electrode is required?
3. Table 21.5 mysteriously arrives at two questionable conclusions. First, the voltage drop of the GEC, based on short-time current rating, should not exceed 40 volts. Why not 30 volts or 50 volts? Second, that the resistance of the GEC, when it exceeds 100 ft, should not exceed the resistance of 100 ft of the conductor specified in the table. Why not consider the total resistance of the path to ground where parallel paths exist?
4. Exactly what does the short-time current rating signify? Using the voltage drop formulas from the UGLY Book, I am unable to duplicate the author's voltage drop for the various conductors.
Thanks for your comments and
Happy New Year!
Brian Dolan