200A 4 pole main

Electriman

Senior Member
Location
TX
Greetings,

I am looking at a house that the service panel main breaker is 4 pole 200A instead of 2 pole 200A. Can I replace it for a 2 pole 200A?I would like to make some space to add an EV charger.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is it a 200A breaker that takes up 4 slots/spaces? Typically when we say pole it’s number of conductors, ie a 4 pole xfr switch that switches the neutral.
So it may be possible to install a smaller 200A main, need make, model and age of panel.
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's likely a GE 200 amp, 2-pole main factory made from 4-100 amp units. It's not a 4 pole circuit breaker.

120.jpg

thqmv1_2.jpg
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Years ago, I asked a company engineer about those breakers. He said two of the poles are basically 100a breakers and the other two are parallel switches.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Years ago, I asked a company engineer about those breakers. He said two of the poles are basically 100a breakers and the other two are parallel switches.
I don't believe that. It looks like 4-100 amp breakers with two in parallel for each pole.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I agree. The plug-in connection is usually the limiting factor. I don't know of any that are rated above 150A.
There are a couple that exist (Siemens QN and Eaton BJ). But they require a double column style panelboard configuration and thus wouldn't work in any of the single column meter/mains that use the aforementioned 4-pole breakers direct to the busbar.

Edit: or rather, those are also basically 4 space breakers.
 

norcal

Senior Member
Can I replace it with two space breaker 200A? Clearly it takes 4 spaces.
Where are you going to find a 200A breaker only using 2 spaces, have seen a BR 150A breaker only requiring 2 spaces, but BR is is not classified for Siemens enclosures. As others have said, twin breakers are the answer, cheaper & easier then trying to substitute the main.
 