200A 4 pole main

Electriman

Senior Member
Location
TX
Can we install twin or tandem breakers in this panel or should I check it with the manufacturer or labeling to see if they allow it?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Can we install twin or tandem breakers in this panel or should I check it with the manufacturer or labeling to see if they allow it?
We would need to see the label or know the model number to answer that.

Look for numbers like 3030 (no tandems) or 3040 (10 tandems).
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Can we install twin or tandem breakers in this panel or should I check it with the manufacturer or labeling to see if they allow it?
ALWAYS check with the manufacturer to see if they allow it. That process MIGHT be as simple as just reading the label they put on the inside of the door showing you the bus arrangement. But if that label is gone, it becomes a lot more difficult.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
What I see with siemens is that the panel and breaker rated at 10kaic has a 2 space main and at 22kaic it has 4 space main. Not sure if same with other mfg.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Can we install twin or tandem breakers in this panel or should I check it with the manufacturer or labeling to see if they allow it?
Read the label on the inside of the cover, it will tell you the Max branch circuit size and type allowed in this panel. Most of this style are limited to 100 amp max branch circuits and tell you were it needs to be placed on the bussing.
 