Agreed in general; I'm hoping to not have to do a load calc for the permit. A dryer won't restart, but a water heater will, and there are two 60a breakers, even though only one is labeled heat.
The pic is a bit blurry, but the 2-poles are: Dryer 30; Water heater 30; Heat 60 (or 50); Unlabeled 60; Range 50 (or 60!). There is also a Homeline breaker. If I get the job, I will check everything.
The customer told me (and it's obvious) is is not the original service; I'm guessing it was an illegal upgrade. Too bad it wasn't done correctly the first time. That might have saved me some time.
I would like a couple of opinions on price. I'm at an even $2K right now, not including the permit and attending inspection(s), removing the existing transfer switch, or any wall patching to be done.
I will need to supply the new service cabling, generator feeder and control wiring, re-route the grounding electrodes to the ATS, separating grounds and neutrals, and of course, the rest of the labor.