Greetings,
I recently had an inspector comment that the 200A Disconnect Switch (Non-Fused) that was installed is inadequately protected by the 80% rated 225AT Feeder Breaker. I'm confused as to why this is considered unprotected as the breaker should trip at 0.80 x 225A = 180A. Does anyone know why this is considered unprotected or if there is a section in the NEC that specifically allows this installation. Not that it matters at this point, but the actual load of the connected device is only around 120A.
All help is appreciated!
I recently had an inspector comment that the 200A Disconnect Switch (Non-Fused) that was installed is inadequately protected by the 80% rated 225AT Feeder Breaker. I'm confused as to why this is considered unprotected as the breaker should trip at 0.80 x 225A = 180A. Does anyone know why this is considered unprotected or if there is a section in the NEC that specifically allows this installation. Not that it matters at this point, but the actual load of the connected device is only around 120A.