kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
That reduced voltage is separately derived within the system. Controls current is returning to the SDS source within the equipment, likely a transformer with 240 volts on the primary side.What I’m referring to is the fact that the controls on the inside are not 240 volts. So I understand it steps down somewhere so where does the non 240 current go on it’s way back to the pole. Do I need to be running an insulated neutral to the disconnect or is it really just 2 hots and a ground that only carries current in the event of a fault?
Never seen a mini split that needed anything but 240 volt two wire for the supply. My point earlier was because some these are international designed, if one the supply terminals is marked "N" it would be where you should put the grounded conductor in say European countries where you have 240 single phase with one conductor grounded.