J Jerome Shepard Member Location Wisconsin Nov 12, 2019 #1 What size conductors are required to feed a load center with a 200a main breaker from a 200a main disconnect, all within 75 feet
What size conductors are required to feed a load center with a 200a main breaker from a 200a main disconnect, all within 75 feet
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Nov 12, 2019 #2 How about giving us your answer first.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 12, 2019 #3 Is it a dwelling unit? Calculated load?
Strombea Senior Member Location Prescott, Arizona, USA Nov 12, 2019 #5 Hahaha no easy answers!! Simple chart should do the trick copper: 3/0 for everything except residential service feeders to entire home you can use 2/0.
Hahaha no easy answers!! Simple chart should do the trick copper: 3/0 for everything except residential service feeders to entire home you can use 2/0.
kwired Electron manager Location NE Nebraska Occupation EC Nov 13, 2019 #6 Majority of time you will need 3/0 copper or 4/0 aluminum. But there are many possible conditions that may require adjusting the results and you give us no details to tell if we may need to make such adjustments.
Majority of time you will need 3/0 copper or 4/0 aluminum. But there are many possible conditions that may require adjusting the results and you give us no details to tell if we may need to make such adjustments.