G gwmobx New member Location Kill Devil Hills NC Dare Mar 26, 2013 #1 Does a 200A Service with a 200A Disconnect installing 4/0 SER from the disconnect to the panel need to be derated ?
Does a 200A Service with a 200A Disconnect installing 4/0 SER from the disconnect to the panel need to be derated ?
roger Moderator Staff member Location Fl Occupation Retired Electrician Mar 26, 2013 #2 Read 310.15(B)(7) and take special note of how it defines "Main Power Feeder". Roger
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 26, 2013 #3 gwmobx said: Does a 200A Service with a 200A Disconnect installing 4/0 SER from the disconnect to the panel need to be derated ? Click to expand... IMO, no it does not if it qualifies as the main power feeder that Roger was talking about. Nowhere in Table or Article 310.15(B)(7) does it state that de-rating shall be considered.
gwmobx said: Does a 200A Service with a 200A Disconnect installing 4/0 SER from the disconnect to the panel need to be derated ? Click to expand... IMO, no it does not if it qualifies as the main power feeder that Roger was talking about. Nowhere in Table or Article 310.15(B)(7) does it state that de-rating shall be considered.