I'm told i can use 2/0 cu THHW for a 200A service. Why is this if according to table 310.15 (B) (16) 2/0 is rated 175A?
I'm told i can use 2/0 cu THHW for a 200A service. Why is this if according to table 310.15 (B) (16) 2/0 is rated 175A?
This:I'm told i can use 2/0 cu THHW for a 200A service. Why is this if according to table 310.15 (B) (16) 2/0 is rated 175A?
See 310.15(B)(7) for dwelling unit services.
I'm told i can use 2/0 cu THHW for a 200A service. Why is this if according to table 310.15 (B) (16) 2/0 is rated 175A?
See 310.15(B)(7) for dwelling unit services.
Not finding 310.15 (B) (7)? 2014 code.
Is it a dwelling?
it is not a family dwelling.
it is not a family dwelling.