In looking over the changes in the 2011 I want to make sure I have it correct.
338.10 (B)(4)(a) is now stating that the amp rating of SE can now go back to the 75 deg column as long as it is not installed in thermal insulation.
So dose this mean that if you install a 200 meter/combo with feed through lugs and the SER doesn't run through thermal insulation we can go back to using 4/0al or doing 2 back to back panels on a 320amp service as long as 240.4 is met?
338.10 (B)(4)(a) is now stating that the amp rating of SE can now go back to the 75 deg column as long as it is not installed in thermal insulation.
So dose this mean that if you install a 200 meter/combo with feed through lugs and the SER doesn't run through thermal insulation we can go back to using 4/0al or doing 2 back to back panels on a 320amp service as long as 240.4 is met?