2011 nec clarification (current carrying conductors)

Merry Christmas
Status
Not open for further replies.

robperkins146

New member
Location
Decatur, il
For calculating the derating based on the number of current carrying conductors. .
A scenario:
installing high bay lights with a switched hot, an unswitched hot (for emergency lighting on the same high bay light, it charges a capacitor which illuminates a seperate bulb that clips on the lens in the event that power is lost), we won't muddy the water with neutrals.

I believe this is 2 current carrying conductors, am I correct?

Thanks in advance,
Rob Perkins
 
With what you have described (and not muddying any water with neutrals) I would tend to agree.

Pete
 
If the unswitched conductor is the same circuit as the switch conductor. then I believe, that the intent is to call that 1 CCC. The problem is the code does not make that distinction. The same question is often asked about 3 way switches or a conduit with one feed and 6 switch legs all the same circuit. IMO, these should not be counted but per NEC they are counted.
 