Greetings FP Stab lok, Aka Federal Noark AKA Federal pioneer NOW Schneider Electric (also Square D) AFCI breakers are available at big orange box stores up North:
https://www.homedepot.ca/en/home/p.single-pole-15-amp-stab-lok-arc-fault-circuit-interrupter-breaker.1000112733.html
A few FP two pole breakers had a glitch in the late 1970's got bad press and deserved it, problem got fixed, fixed breakers had 'pink dot' from then on in 80's but alas brand never recovered so not sold in US markets. Same internals as Square D.
Many old breakers are not marked so 5kAIC interrupting rating (NEC 110). Utility comes along in 1990's puts in more energy efficient transformer tells no one as they are not required to, now 15-20 kAIC fault current exceeds old breakers original rating. Breaker trips blows apart. Manufacturer blamed for 40 year old 5kAIC breaker blowing apart with 25kVA energy saving transformer 18kAIC.
Code did not get serious about fault current till 1975.
Newer FP breakers have 10kAIC rating. UBI replacements even do. Still not enough to be used as one of the 6 'Mains' in a split buss panel with modern utility transformer.
Its dead brands like Zinsco and Pushmatic where you need 2 ckt sub panel for AFCI.
Zinsco breakers came with copper buss clip or Aluminium Zinsco MFR instructions state use proper clip for buss, I.E. copper-copper or aluminium-aluminium. Zinsco Panels accept both types people dont read. Dissimilar metals corrode buss. Panel fire and failure.
Meanwhile Europe and the rest of the world discovers a 20ma GFCI does the same thing as an AFCI and cost 1/3 as much.
Just my 2 cents.