Dennis, it is for both.
I spoke with this poster and what he wanted to do was to use the equipment grounding conductor between a transfer switch(service rated) and an panel that was the main service panel. When he added the transfer switch it was difficult to move the grounding electrode conductor from the now subpanel so he just upsized the equipment grounding conductor to the panel and connected it to the busbar on the subpanel where the original grounding electrode conductor was connected. Although this would probably work fine I feel that it is still a violation using the ground bar as a splice to make the grounding electrode conductor continuous.