This concept comes from a guy named Corwin (as I recall)  - An electrician that was getting close to retirement maybe 35 - 40 years ago when I met him.  I recall him telling me he had license #10.
The Corwin Theory was to upsize the conductors for voltage drop based on:
Distance divided by Voltage = number of wire sizes to jump
Multiples of 120V for voltage >>> match up with multiples of 100 feet.
So for 120V, 20A circuit, over 300 feet, under 400 feet is stepped up 3 wires sizes.  So 12, 10, use #8.
For a 480V, 50A circuit, say a 30hp motor, over 400 feet, under 800 feet, bump one wire size.  So, 8, use #6
For 240V, 200A, over 1000 feet, under 1200 feet, bump 5 wire sizes.  So 2/0, 3/0, 4/0, 250, 300, use 350kcmil
Put up a spread sheet,  Use the table 8 resistances. Have it calculate the VD.  See what the percentages are.  If they are as I recall, they will be in the 3% - 5% range.  You would apply the number of steps the current carrying conductors would be sized up to the EGC.
If this ever got accepted, just think where it will be in a 100 years.  You will be in the same class as the guy that came up with the 25ohm ground rod number - etched in historical stone.
So why don't you do this he asked?  Well, this is about as close as I can get to the process - I'm getting a bit queasy already.  Better somebody that cares.
ice