Don't kill the messenger... :lol:Well that strikes me as a screw up.
Don't kill the messenger... :lol:Well that strikes me as a screw up.
But it won't apply to a fire pump where voltage drop compensation is NEC required
That's what I was getting at in post #14.
Does this really need to be this convoluted?
But it won't apply to a fire pump where voltage drop compensation is NEC required
That is correct.
Now I'm rethinking that position...Well that strikes me as a screw up.
Correct. A code forced upsizing of ungrounded conductors does not require the EGC to be upsized... but not limited to just under 2014... essentially all editions back to 1999 (or 2002 ?)
250.122(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately accord-
ing to the circular mil area of the ungrounded conductors.
Now I'm rethinking that position...
It may apply. The wording refers to minimum ampacity... not minimum code required size.
That makes the whole issue a conundrum without resolution.
If you take the wording literally, yes.I disagree for the several editions prior to the 2014 where the words simply stated "Where ungrounded conductors are
increased in size". Using #10's on a 20 amp circuit would be an increase in size requiring a #10 EGC as well.
2008 NEC:
250-955. Size of Equipment Grounding Conductors. The size of copper,aluminum, or copper-clad aluminum equipment grounding conductors
shall not be less than given in Table 250-95.
Where conductors are run in parallel in multiple raceways, as permitted
in Section 310-4, the equipment groundihg conductor, where
used, shall be run in parallel. Each parallel equipment grounding conductor
shall be sized on the basis of the ampere rating of the overcurrent
device protecting the circuit conductors in the raceway in accordance
with Table 250-95.
When conductors are adjusted in size to compensate for voltage drop,
grounding conductors, where required, shall be adjusted proportionately
in size.
(b) Adjustment for Voltage Drop. Where conductors are
adjusted in size to compensate for voltage drop, equipment
grounding conductors, where installed, shall be adjusted pro-
portionately according to circular mil area.
(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately accord-
ing to circular mil area of the ungrounded conductors.
:rotflmao:Don't screw things up, we were making progress.
Call me doubtful they put that much thought into it.
Stay tuned for the next episode in 2017, the CMP needs to leave cliff hangers so we will buy the next book.
And I disagree right back at you. :happyyes:I disagree for the several editions prior to the 2014 where the words simply stated "Where ungrounded conductors are
increased in size". Using #10's on a 20 amp circuit would be an increase in size requiring a #10 EGC as well.
And I disagree right back at you. :happyyes:
That has been my biggest problem with it since they tried to address the issue - and I have always brought up that same example when this topic is brought up.Table 250.122 should be reworked so that the size of the EGC is based on the size of the ungrounded conductor and not on the rating of the OCPD. All of this goes away if you do that. Especially the crazy part where a #6 on a 20 amp breaker requires a #6 EGC and that same #6 on a 60 amp breaker only requires a #10 EGC.
sounds like they possibly needed to adjust ampacity for the first part of the run because of number of current carrying conductors.I've seen contractors run all number 10 hr.from the panel to a trough 10 feet outside the electrical room than change to 12 wire from there .
this has always bothered me ,should it