Julie,
I don't understand. It is first by Code Making Panel and then by code Article and Section. And if you are looking for a comment on a proposal that was accepted at the ROP stage it is even easier. You first download the draft copy. Each proposed change is show along with the proposal number for that change. You then just search the ROC for that proposal number.
If the following is the change you are talking about, you would search the panel 4 comment for proposal 4-253. There were two comments submittd on that change.
I don't understand. It is first by Code Making Panel and then by code Article and Section. And if you are looking for a comment on a proposal that was accepted at the ROP stage it is even easier. You first download the draft copy. Each proposed change is show along with the proposal number for that change. You then just search the ROC for that proposal number.
If the following is the change you are talking about, you would search the panel 4 comment for proposal 4-253. There were two comments submittd on that change.
690.12 PV Arrays on Buildings Response to Emergency Shutdown. . For PV Systems installed on roofs of buildings, photovoltaic source circuits shall be deenergized from all sources within 10 seconds of when emergency shutdown is initiated or when the PV power source disconnecting means is opened. When the source circuits are deenergized, the maximum voltage at the module and module conductors shall be 80 volts. [ROP 4?253]