D dontknow Member Location beachwood Nov 23, 2020 #1 Does this code article require the use 19 stranded Pv wire in trackers? Or is this a ”shall be” situation. 690.31(E) table
Does this code article require the use 19 stranded Pv wire in trackers? Or is this a ”shall be” situation. 690.31(E) table
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 23, 2020 #2 I see it as saying you can use PV wire where the stranding of that wire complies with Table 690.31(E)
I see it as saying you can use PV wire where the stranding of that wire complies with Table 690.31(E)