What would what be?Ok Then what would it be!
What would what be?Ok Then what would it be!
I thought the NEC was not a design guide!
It depends somewhat on the CMP. CMP14 was heavy into using Section 90.1(C). Those CMPs that are especially heavy into residential or light commercial are more likely to give design directives. A few unnamed aren't quite sure.
As best I can tell, the intent was to include any work surface similar to a countertop. The term countertop is not defined in the NEC and the definition varies in dictionaries.I understand that you can't do it even under the 2014 but I was wondering if they were trying to clarify it...Did a great job of it if that was their intent.
I ordered the 2017 NEC book with the pdf from Nfpa.org. I got an email that the pdf is available for download. I just downloaded it-- simple easy. Just thought you would all like to know
What would what be?
It would be a 3' wall space. Being more than 2' wide, at least one receptacle is required within that space to satisfy 210.52(A).That 3 foot space be. How would it be counted or used as far as receptacles
How much is it?
I ordered the 2017 NEC book with the pdf from Nfpa.org. I got an email that the pdf is available for download. I just downloaded it-- simple easy. Just thought you would all like to know
Free tabs not advertised on multi-product page:NFPA.ord They have a special where you get the tabs for free--- http://catalog.nfpa.org/NFPA-70-Nat...tion-with-FREE-NEC-Tabs-P14077.aspx?icid=D682
Seems like you wuill have to go to this page and then choose products by topic
Free tabs not advertised on multi-product page:
http://catalog.nfpa.org/NFPA-70-Nat...-Softbound-2017-Edition-P16529.aspx?icid=B484
Did you get the tabs for the PDF version as well?NFPA.ord They have a special where you get the tabs for free--- http://catalog.nfpa.org/NFPA-70-Nat...tion-with-FREE-NEC-Tabs-P14077.aspx?icid=D682
Seems like you wuill have to go to this page and then choose products by topic
Did you get the tabs for the PDF version as well?
I would like some comment on this one please
Here is an interesting one. I read this to mean if we have a desk area with receptacles at the desk top then the space below may need a receptacle if it falls into the standard distance rule req. for recep. on a wall. That's nuts. I can see if it were in a cabinet with a door---Maybe I am reading this incorrectly
Greetings Dennis,
The language was presented by my friend Mr. Brian Rock to simply acknowledge that the receptacles required by 210.52(C) can't be used to meet the requirements of 210.52(A), which as you eluded to was near the intended language of previous cycles as far as the intent of not allowing such a receptacle to serve such a use. With the addition of the term "similar work surfaces" the submitter was trying to address the need for receptacle in those similar work surface areas to those in 210.52(C), needing to fully meet the spacing and intent of 210.52(C).
So if the space in question is considered a wall space then it would need to met the spacing requirements of 210.52(A) as you have stated. Again it was simply to clarify that the new countertop surfaces or similar work spaces in those same specific locations are required to meet 210.52(C) and that again they are not to be used to meet any of the requirements of 210.52(A).
So I think you nailed it from what I can gather.
agreed. In short it was a CYA from a previous change. However, some on the CMP disagreed and felt that adding the new terms "similar work surfaces" or something to that effect would cause confusion since no definition exists. But only two voted against it and it passed mustard.Thanks Paul. At first I was taken for a loop on it but then I did feel that the intent was as you stated.
Greetings Dennis,
The language was presented by my friend Mr. Brian Rock to simply acknowledge that the receptacles required by 210.52(C) can't be used to meet the requirements of 210.52(A), which as you eluded to was near the intended language of previous cycles as far as the intent of not allowing such a receptacle to serve such a use. With the addition of the term "similar work surfaces" the submitter was trying to address the need for receptacle in those similar work surface areas to those in 210.52(C), needing to fully meet the spacing and intent of 210.52(C).
So if the space in question is considered a wall space then it would need to met the spacing requirements of 210.52(A) as you have stated. Again it was simply to clarify that the new countertop surfaces or similar work spaces in those same specific locations are required to meet 210.52(C) and that again they are not to be used to meet any of the requirements of 210.52(A).
So I think you nailed it from what I can gather.
Any idea of the logic of why a receptacle about right above the end of a countertop can't serve the first two feet of 210.52(C) counter top and the first six feet 210.52(A) wall on the other side? This presuming the wall is still in space allowed to be on the same circuit.
As is worded now for 2017, one could still put a two gang box or even turn a single gang box horizontal and put centerline directly over the counter edge so that one receptacle is over the counter and the other is past the counter and you still are compliant but essentially have the same thing, it just took a little more care in exact placement.
IMO this is encroaching too far on NEC being a design manual.
I agree that reading the official comments and proposals or inputs does at least help with figuring out what the intent was. Won't agree that what goes into final print always meets those goals though. And sometimes there are other effects from a change they never considered - this might be one of them. Sounds like their primary focus was on the built in desk in kitchen areas, and the way it ended up that next six feet of wall adjacent to the counter unintentionally was effected.Greetings kwired,
Well I have found that when I try to enlist my own logic to examine someone else's logic that never works out well for me. I can only present what is discussed or what is recorded in the submittal and justification process of the code making process, and we all can view that on TarraView (think thats the name of it) when it works and it does for the most part. I think there is nearly anything in the NEC that if you think long and hard about it can be circumvented in some fashion, so again I prefer to keep with the intent and let everyone else have their own opinions on it. The intent was to not co-mingle the two requirements for serving the needs of 210.52(C) and 210.52(A). The additional statements " or similar work surface" has been coming a long time for those folks who have the built in desks in kitchens and dinning rooms so this was a natural progression. Quite frankly I think it was the best language they could muster on that day and it works for the most part.
my own logic is that in the 2014 NEC it was presented that a countertop receptacle (required by 210.52(C)) could not serve the requirements of 210.52(A). With the addition of the "similar work surface" the CMP had to write it so that it keeps the integrity of what was established in the 2011 NEC via 210.52(A)(4) and include the work surfaces that tend to (in the proponent for the change) be left without receptacles that should (agree or not) on the small appliance branch circuit.
Full disclaimer - This is not what Mr. Rock has stated or his logic or the CMP's logic....it is my analysis of their intent only.
Hope it was helpful and if not...my apologies for my long winded response.